We have a school system and all of a sudden (about the time it started getting COLD outside) they complained about a 65ppm color machine (20amp) that starts firing off
fuser errors. Tech replaced the fuser unit and a few days later it did it again. I told him to check the AC socket for a neutral-ground voltage. Also asked if it has an ESP filter
on the circuit and he said yes. Brought it in and I checked. Had over 100 entries in the last 9 months. About 30 for a month. Most were surge/drop outs. This ESP didn't have
the neutral to ground because it was an older one. Tech went back, showed them the printout and he checked the N-G and when the machine was running it was spiking OVER
four volts! He told them to have an electrician check the circuit to make sure it was a dedicated outlet.
Couple days later they said the machine did it again, electrician said the outlet was good bla bla bla.
Couple more yes it is, no it isn't and then one of my supervisor techs went there and had the school electrician with him and he said after seeing the N-G voltage, "oh, looks like
you have a common mode issue" (tech's jaw hit the floor when he said that...DUH! someone gets it).
But the school said it wasn't a problem, so, we pulled a like machine from the other side of the school that service history showed NO issues, and swapped the machines.
NEXT day the machine that has NEVER had a problem, had the same fuser code as the original machine.
And here's the kicker. The school said "oh, well maybe that outlet isn't a dedicated line?" YA THINK?
Most likely some "Susie secretary" doesn't like the cold, plugged in her space heater and is pulling a bit too much juice.
That, or the wiring in the building needs to be replaced.
THIS is why my hair is gray!
fuser errors. Tech replaced the fuser unit and a few days later it did it again. I told him to check the AC socket for a neutral-ground voltage. Also asked if it has an ESP filter
on the circuit and he said yes. Brought it in and I checked. Had over 100 entries in the last 9 months. About 30 for a month. Most were surge/drop outs. This ESP didn't have
the neutral to ground because it was an older one. Tech went back, showed them the printout and he checked the N-G and when the machine was running it was spiking OVER
four volts! He told them to have an electrician check the circuit to make sure it was a dedicated outlet.
Couple days later they said the machine did it again, electrician said the outlet was good bla bla bla.
Couple more yes it is, no it isn't and then one of my supervisor techs went there and had the school electrician with him and he said after seeing the N-G voltage, "oh, looks like
you have a common mode issue" (tech's jaw hit the floor when he said that...DUH! someone gets it).
But the school said it wasn't a problem, so, we pulled a like machine from the other side of the school that service history showed NO issues, and swapped the machines.
NEXT day the machine that has NEVER had a problem, had the same fuser code as the original machine.
And here's the kicker. The school said "oh, well maybe that outlet isn't a dedicated line?" YA THINK?
Most likely some "Susie secretary" doesn't like the cold, plugged in her space heater and is pulling a bit too much juice.
That, or the wiring in the building needs to be replaced.
THIS is why my hair is gray!