If it is indeed a sub panel, NO. From National Electrical Code 214:
At the service panel (ONLY AT THE SERVICE PANEL - HUGELY IMPORTANT) the neutral bus bar is bonded to ground. However, any sub-panel after the primary service from there MUST have an isolated neutral. DO NOT DO NOT DO NOT bond neutral to ground in a sub-panel.
I have encountered electrical outlets with floating grounds, ground terminal not connected to the ground bus at the AC panel. I have actually seen a "ground" pin on an outlet that measured half way between hot and neutral.
If it is indeed a sub panel, NO. From National Electrical Code 214:
At the service panel (ONLY AT THE SERVICE PANEL - HUGELY IMPORTANT) the neutral bus bar is bonded to ground. However, any sub-panel after the primary service from there MUST have an isolated neutral. DO NOT DO NOT DO NOT bond neutral to ground in a sub-panel.
I have encountered electrical outlets with floating grounds, ground terminal not connected to the ground bus at the AC panel. I have actually seen a "ground" pin on an outlet that measured half way between hot and neutral.